VFD test motor
chaterpilar
Saudi Arabia
I have a 75 kw rated 380 volts VSd wich i want test using a small motor 7.5 hp in the workshop before sending it to site.
Now, is there any limit to the minimum size of the motor that can be used on test ( apart from the minimum current setting of the VFD)?
Cheers.
Cheers.
There may be but we routinely test drives up to several hundred kW using a 4kW motor. On one recently, we did use a 30kW motor but that was only because we could reconnect the windings to get the voltage we wanted - 690V in that particular case.
Some drives has an underload feature to detect loss of load. The default parameter set is usually, if not always, to have that function disabled.
If it is V/Hz I doubt you will have any issues. If it is sensor-less vector then they recommend not going below 1/3 of the drives hp rating. The drive has a hard time determining motor positioning when it is too same.
For a test to ensure basic operation of controls, you can usually select a scalar operation. I think that's what chaterpilar was seeking to do.
But I agree that it's a different matter if you want performance testing.