Breakers for C1D2 with switched neut

Status
Not open for further replies.

s-park-er

Member
Location
Oroville, CA
Occupation
Building mechanic - specialty problem-solver.
Can I use a 3-pole panel and breakers on a 240V 1ph installation utilizing the third buss to provide grounded conductor interruption? (Specifically Sq-D QO series) or do I have to use the more expensive switched neutral breakers in a 2-pole single phase panel? :roll:
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
You want to use the three busses as L1, L2 and N?

I don't see why you can't. You can use a 3 phase panel for corner grounded systems. Not much difference.

I am curious though.
 
Last edited:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
You want to use the three busses as L1, L2 and N?

I don't see why you can't. You can use a 3 phase panel for corner grounded systems. Not much difference.

I am curious though.
I'm assuming he's trying to comply with 514.11 since it is the only case where classified locations require opening the neutral; i.e., it isn't a general Art 500-501 requirement. The most commonly used device though is a 3-pole, maintain on/maintain off, push-button switch.

Nevertheless, I agree with you; in absence of a 110.3(B) issue, a 3-pole breaker with the center pole used to open the neutral would work.
 

s-park-er

Member
Location
Oroville, CA
Occupation
Building mechanic - specialty problem-solver.
That's exactly what I want to do. I just didn't know if that would be considered as back-feeding the breaker on the neutral leg? I believe QO's can be back fed anyway.
 