I would like your comments on the following case:
1.- In a new comercial building (like a hotel for eldery people) the maintenance people detected a money penalty of the electric utility for ?low power factor? ( 0.34 ).
2.- The building is new and by the moment almost no electric load. They have a 750 KVA substation (23 Kv to 220 / 127 V) and from 6 to 11 kW m?ximum demand.
The ?low power factor? sense by the utility was due to the transformer magnetization current
The load of 6 to 11 kw was almost lightning and some contacts so NO induction loads
The Capacitor vendor is saying that in order to shift fro 0.34 to 0.95 the p.f. he will recomend a 30 KVAR capacitor capacity ( not automatic)
K=TAN(ACOS(0.34))-TAN(ACOS(0.95))= 2.437
KVAR= 2.437 X 13 KW = 31.7 KVAR
Questions
1.- Whats your opini?n about the size of the fix capacitor ? . Incidently this low load situation will probably last 1 ? 2 years
2.- We are planning to put to work just half of the 30 KVAR capacity and check the p.f. in the utility meter.
3.- If so, is it advisable to design and install now an automatic capacitor and add some modules as they are needed . Say start with 30 KVAR up to 60 KVAR ?
Regards
1.- In a new comercial building (like a hotel for eldery people) the maintenance people detected a money penalty of the electric utility for ?low power factor? ( 0.34 ).
2.- The building is new and by the moment almost no electric load. They have a 750 KVA substation (23 Kv to 220 / 127 V) and from 6 to 11 kW m?ximum demand.
The ?low power factor? sense by the utility was due to the transformer magnetization current
The load of 6 to 11 kw was almost lightning and some contacts so NO induction loads
The Capacitor vendor is saying that in order to shift fro 0.34 to 0.95 the p.f. he will recomend a 30 KVAR capacitor capacity ( not automatic)
K=TAN(ACOS(0.34))-TAN(ACOS(0.95))= 2.437
KVAR= 2.437 X 13 KW = 31.7 KVAR
Questions
1.- Whats your opini?n about the size of the fix capacitor ? . Incidently this low load situation will probably last 1 ? 2 years
2.- We are planning to put to work just half of the 30 KVAR capacity and check the p.f. in the utility meter.
3.- If so, is it advisable to design and install now an automatic capacitor and add some modules as they are needed . Say start with 30 KVAR up to 60 KVAR ?
Regards