Has anyone installed GE kv2c meters? these are pulse rated and come with a wire harness with 9 wires, Our energy management company is having a real time of it trying to find the outputs that will give them the readings they need
 

mivey

Senior Member
This?

kV2 S I/O Cable
Signal Name WireColor PinNumber
Y1_OUT Yellow 4
Z1_OUT Black 6
Y2_OUT Grey 10
Z2_OUT Blue 12
K1/K2_OUT Red 8
Z3_OUT Orange 14
K3_OUT Brown 16
RTP+ Violet 2
RTP- Green 1

add: If you want KYZ then use Red, Yellow, Black. If you just want KY then just use Red & Yellow.
 
Last edited:

mivey

Senior Member
Not sure what you are trying to do but we have used these pulse isolation relays with with KYZ from the meter and KY or KYZ to the customer for load control:
http://www.solidstateinstruments.com/

These devices provide additional protection and I would not recommend using the pulses directly from the meter.
 