Depends. FAR 107.14 Airport AOA access doors are to be fail secure. They get an exemption. I bet bank doors and prisons get a break also, but I wouldn't know much about those doors.
You are correct about the prison which would be classified as an "I" group. Need to see what an airport would be classified as. Probably a B and A.
1008.1.3.4 Access-controlled egress doors. The
entrance doors in a means of egress in buildings with an
occupancy in Group A, B, E, M, R-1 or R-2 and entrance
doors to tenant spaces in occupancies in Groups A, B, E,
M, R-1 and R-2 are permitted to be equipped with an
approved entrance and egress access control system
which shall be installed in accordance with all of the following
criteria:
1. A sensor shall be provided on the egress side
arranged to detect an occupant approaching the
doors. The doors shall be arranged to unlock by a
signal from or loss of power to the sensor.
2. Loss of power to that part of the access control system
which locks the doors shall automatically
unlock the doors.
3. The doors shall be arranged to unlock from a manual
unlocking device located 40 inches to 48
inches (1016mmto 1219 mm) vertically above the
floor and within 5 feet (1524 mm) of the secured
doors. Ready access shall be provided to the manual
unlocking device and the device shall be
clearly identified by a sign that reads ?PUSH TO
EXIT.? When operated, the manual unlocking
device shall result in direct interruption of power
to the lock?independent of the access control system
electronics?and the doors shall remain
unlocked for a minimum of 30 seconds.
4. Activation of the building fire alarm system, if
provided, shall automatically unlock the doors,
and the doors shall remain unlocked until the fire
alarm system has been reset.
5. Activation of the building automatic sprinkler or
fire detection system, if provided, shall automatically
unlock the doors. The doors shall remain
unlocked until the fire alarm system has been reset.
6. Entrance doors in buildings with an occupancy in
Group A, B, E or M shall not be secured from the
egress side during periods that the building is open
to the general public.