Here's my situation: I am looking to feed a 200A load off a 500kVA 480/208V transformer. Primary side is a 800A breaker I believe. Right now there is a 1000A disconnect fused at 600A on the secondary. According to 250.21, with the 10ft tap, I would be at 184.8A. It also says you can't extend the secondary feeders past the device it feeds. I assume then I can't tap off the secondary and then feed a 200A disconnect to feed my load. Maybe I'm reading this wrong.
My new plan then is to have a 200A panelboard in-line with the 600A fuses to step it down and then feed my 200A non-continuous load. Does this work? Also, would I even need a panelboard? Couldn't I just have a box with lugs to land the 600A wire and then step down to a 200A breaker in a box? Is there a better solution that I'm missing.
My new plan then is to have a 200A panelboard in-line with the 600A fuses to step it down and then feed my 200A non-continuous load. Does this work? Also, would I even need a panelboard? Couldn't I just have a box with lugs to land the 600A wire and then step down to a 200A breaker in a box? Is there a better solution that I'm missing.