is it legal or safe to run NM wire in the crawl space of a single family dwelling set on a steel frame?-confused:
Why wouldn't it be?
is it legal or safe to run NM wire in the crawl space of a single family dwelling set on a steel frame?-confused:
So a crawl space is now considered a damp location? I can't find that in the 2008 code but i may have missed it.
334.10(B) Type NMC. Type NMC cable shall be permitted as follows:
(1) For both exposed and concealed work in dry, moist, damp, or corrosive locations, except as prohibited in 334.10(3)
If this is a manufactured home then yes it is, and HUD codes (CFR 24 3280) apply, if this is a modular or other type of structure then no, local codes apply.
If it is a manufactured house, it will have a RED HUD plate on the outside of it somewhere.
since romex is not rated for damp locations running nm through a crawl space is a no-go DA
They do not use red tags any more.
"Don't think its a problem, cept under a trailer, which is what I was trying to say in my previous post"
I can find no reason to disapprove this installation (NM). Using 334.10.(A)(1)
Where is 334.10(3) as stated in 334.10(A)(1)?
550.15(H) Under-Chassis Wiring (Exposed to Weather). Where outdoor or under-chassis line-voltage (120 volts, nominal, or higher) wiring is exposed to moisture or physical damage, it shall be protected by rigid metal conduit or intermediate metal conduit. The conductors shall be suitable for wet locations.
Exception: Electrical metallic tubing or rigid nonmetallic conduit shall be permitted where closely routed against frames and equipment enclosures.
This should explain where I was headed.![]()
Who decides whether outdoor or under-chassis wiring is exposed? If it was always, the rule would apply to all under-chassis wiring.This should explain where I was headed.![]()
Oh and Mike P., the HUD label is still required, see:Sec. 3280.11 Certification label., but your right I cant find where it requires it to be red, but we are still getting them that are red?They do not use red tags any more.
Who decides whether outdoor or under-chassis wiring is exposed? If it was always, the rule would apply to all under-chassis wiring.
If anyone is interested, here is an online version, of the CFR Title 24--Housing and Urban Development 3280, 3280.800 to 900 is the electrical requirments, and talking about being behind times, this is the moct recent realise, and it is dated 2004, but is still referanceing the 1993 NEC:roll:
see Sec. 3280.801 Scope.
it can be downloaded (each section) as text or PDF
Oh and Mike P., the HUD label is still required, see:Sec. 3280.11 Certification label., but your right I cant find where it requires it to be red, but we are still getting them that are red?
Wayne
I was wrong (about the red). Imagine that?
http://www.ibts.org/certification_label.shtml
"Each manufactured home built in the United States after June 15, 1976 has a data plate. The data plate includes the manufacturer's certification that the home is designed in accordance with U.S. Department of Housing and Urban Development's construction and safety standards in effect on the date the home was manufactured. HUD Standards include Body and Frame Requirements, Thermal Protection, Plumbing, Electrical, Fire Safety, and other aspects of the home.
The data plate includes the date of manufacture, name and address of the manufacturing plant, manufacturer's serial number and model, a list of certification labels applied to the home, major equipment, roof load, heating/cooling and wind zone information. Also included is the Design Approval Primary Inspection Agency (DAPIA)."
http://www.ibts.org/data_plate.shtml