manual transfer switches
eric -
that's not enough information for us to do us any good - if you some help - tell us a little more about what you are tryin to do
cf
Installing a double throw mts for a generator,which will be used for emergency power during a utility outage the mts will be connected to the main service it has a main breaker for the service disconnect
If your amps and volts do not exceed your ratings, you should be good to go.I think the reason that you don't see it often is cost, 600 volt equipment is higher in cost than your 250 volt equipment. Just my opinion !
Can a mts rated for 277/480v be used for a 120/208v system being that it is rated for up to 600v?
Not in every case, depends on what you have. If there are no relays, CPT's, indicating lights or solenoids in the control circuit then YES.
I have seen GE-Zenith MTS's that use pushbuttons, microprocessor and a solenoid to manually switch the contacts, i.e. the applied voltage has to match the control circuit rating, if there is one.:grin:
TT
I think one issue here is that "manual transfer switch" is too vague a term. It can mean a Double Throw Safety Switch, or, as mentioned above, can mean an electrically operated transfer switch system with manual control operation and without the automatic line sensing feature. Manufactuers such as Zenith and Asco who also make ATS systems tend to refer to the non-automatic electrically operated systems as MTS, whereas people like Sq. D, Siemens and Cutler Hammer, who make Safety Switch disconnects, tend to refer to DT Safety Switches as MTS. Both are right, but the difference can be important when discussing this specific issue.
I think that one issue that can differentiate is the UL listing. The one's refered to by the ATS makers will have a UL1008 rating as a "non-automatic transfer switch", the ones that are DT Safety Switches will have a UL98 rating as a Disconnect Device.