Min. ground conductor size for lightning protection system
anbm
TX
Designer
For lighting protection system, is there a code requirement for min. conductor size that connect all air terminals, equipment on roof, downlead conductor, rods and ground loop? Thanks!
Previous message... I mean " lightning " protection system (NFPA-780 relates) not lighting. Thanks!
You need to contact some of mfg for information or the National Ltg Protection Institute. The NEC won't help you much.
Per NFPA 780-2008
Copper Class I materials
Main conductor, solid strip
Thickness 0.051 in.
Cross section area 57,400 cir. mils
Aluminum Class I materials
Thickness 0.064 in.
Cross section area 98,600 cir. mils
Class II = Structures exceeding 75' in height
Copper Class II materials
Thickness 0.064 in.
Cross section area 115,000 cir. mils
Aluminum Class II materials
Thickness 0.1026 in.
Cross section area 192,000 cir. mils