Minimum Maximum voltage
brian john
Kilmarnock, Va
Retired after 52 years in the trade.
Over the years there have been different numbers bantered around regarding the acceptable minimum and maximum percentages allowed by utilities. I realize this may vary form state to state based on the state corporation commission. But for you area do you have hard fast numbers that are facts not just here say.
I think many POCOs are held to ANSI C84, but you would have to check.
North Carolina PUC
North Carolina PUC
Rule R8-17. Standard voltage.
(a) Each electric supplier shall adopt and file with the Commission standard average service voltages available from its distribution class facilities. The filing shall contain the nominal voltage, base voltage, lower limit and upper limit. The voltage maintained at the point of delivery shall be reasonably constant and variations therein should not normally exceed the limits set forth in this rule.
(1) In order to promote standardization of service voltages, the following standard nominal service voltages are hereby adopted by the Commission as the preferred standard nominal service voltages:
NOMINAL SYSTEM VOLTAGE
Two-wire
Three-wire
Four-wire
Single-Phase Systems
120*
120/240*
Three-Phase Systems
208Y/120
240/120
240
480Y/277
480
600**
2400
4160
4160Y/2400
4800
6900
8320Y/4800
12000Y/6930
12470Y/7200
13200Y/7620
1380
13800Y/7970
20780Y/12000
23000
22860Y/13200
24940Y/14400
34500
34500Y/19920
*see (a)(2) below
** This classification covers the range of nominal voltages from 550 to 600 volts.
(2) Each electric supplier operating within the State of North Carolina under the jurisdiction of the Commission shall offer 120/240 volt, single phase service. No electric supplier shall offer 115/230 volt single phase service or other such similar variant of 120/240 volt single phase service except upon specific authorization of the Commission.
(b) In order to promote harmony between the service of electric suppliers and the utilization voltage requirements of presently manufactured equipment, the following service voltage variations are permitted:
(1) For service rendered for individual residential use or specifically for lighting purposes, the voltage variations shall not exceed five percent (5%) above or below the standard base voltage.
(2) For other service the voltage variations shall not exceed ten percent (10%) above or below the standard base voltage.
(c) An electric supplier may elect to deliver service at a nominal voltage which is not standard on its system. The variation in the nonstandard voltage shall not exceed the limits set forth above for the type of service being rendered.
(d) Upon approval of the Commission and proper notification to its customers a utility may cease to deliver a particular voltage.
(e) Variations in voltage in excess of those specified caused by the addition of customer equipment without proper notification to the electric supplier, by the operation of customer's equipment, by the action of the elements, by infrequent and unavoidable fluctuations of short duration due to system operations, by conditions which are part of practical operations and are of limited extent, frequency, and duration, or by emergency operations shall not be construed a violation of this rule.
(f) Consumers shall select, install, maintain and operate their electrical equipment so as to cause the least interference with the regulation of the electric supply system. Three phase motors in excess of 20 horsepower, single phase motors in excess of five horsepower and other apparatus with high starting or fluctuating currents must be installed in accordance with the supplier's filed tariffs and rules and regulations.
(g) Greater variations in voltage for service to installation which permit greater variations than those required above may be allowed upon specific authorization by this Commission.
(NCUC Docket No. E-100, Sub 9, 4/25/72.)