When you have a 2 wire to 2 wire transformer, primary current directly corresponds to secondary current, so you can use primary OCPD to provide secondary protection.
You are _permitted_ to size the primary OCPD at less than the maximum given in 450; depending upon the situation this _might_ result in the primary OCPD tripping on inrush current, however in my experience with _small_ transformers (25KVA and the like) this has not been a problem even with significantly undersized OCPD, though with an unloaded secondary.
-Jon