inspector 102
- Northern Indiana
Under 230.32 (B), it states that the grounding electrode shall be run with the supply conductors to a detached building. This indicates that a four-wire system is required for all panels installed in a detached garage. If there is only a three wire system (H-N-H), then can you re-establish a grounding electrode at the detached building and if yes, would you bond the grounded conductor and grounding conductor at the detached panel? Would this create a parallel path by bonding the two? If the three-wire is provided, and isolated neutral and ground, would this meet the requirements of 230.32? All confused for now.
