lakee911
- Columbus, OH
Suppose I was running 3#2,1#4G (XHHW), 2"C (PVC) and I need a pull box.
An obvious choice would be a type "C" conduit body. According to NEC 314.28(A)(1), the conduit body can be no less than 8x the largest raceway and I'm allowed to use the minimum size of the raceway that would be required. So, fortunately for this size wire I'm allowed to use a minimum size of 1-1/4"C.
So, 8*1-1/2" = 10"
This conduit body, according to literature is only approx. 8" long, so it can not be used!
Now, what I think is stupid is if I splice my wire, according to NEC 314.28(A)(1), I am allowed to use 6x (rather than 8), so I'm down to 7-1/2", so this would be allowed.
I don't want to splice it though, and I'm not sure that a PVC box exists that would be like 2" or 3" wide by 10" long (or 16 for that matter if it had to be full sized).
I don't get it... Can anyone offer insight?
So, 8*1-1/2" = 10"