Rich Elec.
- Pennsylvania
In the Sept./Oct. IAEI magazine Jim Pauley has an article "Understanding NEC rules about wire temperature ratings, ..."
Page 22 "Derating process example".
Last paragraph: I am going to paraphrase. This are the general ideas, so that I can get my question asked. I don't want to be too wordy.
"110.14 (C)(1) states, ... conductor ampacities used in determining equipment termination provisions shall be based on Table 310.16 as appropriately modified by 3105.15 (B)(1) through (6)."
"Other tables may be applicable for the conductors in a specific environment,"
"For instance, a single conductor installed in free-air may have its ampacity determined by Table 310.17. Examples of those circumstances where this may be useful include ambient derating and installation in a cable tray. However, at the point where the conductor is terminated in equipment, the ampacities of Table 310.16 will govern, This may require that a larger conductor be used or that the conductor size be changed prior to entering the equipment."
My question is: If "this may require that a larger conductor be used or that the conductor size be changed prior to entering the equipment.", in certain installations could the rule at 310.15(A)(2) Ex. apply?
10' or 10% of the circuit length the higher ampacity may be used.
Am I applying this rule correctly?
Thank you,
Rich
Thank you,
Rich