Grounded Conductor
cooldad
Am I required to use a neutral conductor in a 3ph wye (120/208) feeder that will be used to feed a bank of airconditioning units? - no other loads will be used from this sub-panel. grateful if you could comment on this.
Thanks
If your loads do not require a neutral wire, then the feeder or branch circuit need not contain one. Welcome to the forum.
Welcome to the forum! :)
Not if the neutral will not be needed by any loads.
Why was the other duplicate post (located in NEC section) deleted when this is an NEC rule issue and not an engineering/design issue?
Just curious
Just curious
Because it is a design issue. :)
You may want to have a neutral present for future loads or you may not. One design method will cost less than the other.
And another reason was that this thread already had activity.
Roger
Thanks
If you do that, the subpanel, and breakers cannot be slash rated.
Because one is not using the grounded conductor of a Solidly grounded Wye System, does not change the fact the system wiring to the subpanel is still a Solidly grounded Wye system.
Take a look at the second paragraph of 240.85. The issue is the ungrounded conductor in relation to ground, not to the grounded conductor.
What do you mean by slash rated
Some breakers are rated 120/240v, and some 240v. The former relates to line-ground voltage, and the latter to line-line voltage.
The rating here needs to be greater than 120v line-to-ground, at least for any 2- or 3-pole breaker connected to the high leg.