Am I required to use a neutral conductor in a 3ph wye (120/208) feeder that will be used to feed a bank of airconditioning units? - no other loads will be used from this sub-panel. grateful if you could comment on this.

Thanks
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
If your loads do not require a neutral wire, then the feeder or branch circuit need not contain one. Welcome to the forum.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum! :)

Am I required to use a neutral conductor in a 3ph wye (120/208) feeder that will be used to feed a bank of airconditioning units? - no other loads will be used from this sub-panel. grateful if you could comment on this.
Not if the neutral will not be needed by any loads.
 

paul

Senior Member
Location
Snohomish, WA
Why was the other duplicate post (located in NEC section) deleted when this is an NEC rule issue and not an engineering/design issue?

Just curious
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Why was the other duplicate post (located in NEC section) deleted when this is an NEC rule issue and not an engineering/design issue?

Just curious

Because it is a design issue. :)

You may want to have a neutral present for future loads or you may not. One design method will cost less than the other.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
And another reason was that this thread already had activity.

Roger
 

mcclary's electrical

Senior Member
Location
VA
Am I required to use a neutral conductor in a 3ph wye (120/208) feeder that will be used to feed a bank of airconditioning units? - no other loads will be used from this sub-panel. grateful if you could comment on this.

Thanks

If you do that, the subpanel, and breakers cannot be slash rated.
 
If you do that, the subpanel, and breakers cannot be slash rated.



Because one is not using the grounded conductor of a Solidly grounded Wye System, does not change the fact the system wiring to the subpanel is still a Solidly grounded Wye system.


Take a look at the second paragraph of 240.85. The issue is the ungrounded conductor in relation to ground, not to the grounded conductor.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
What do you mean by slash rated
Some breakers are rated 120/240v, and some 240v. The former relates to line-ground voltage, and the latter to line-line voltage.

The rating here needs to be greater than 120v line-to-ground, at least for any 2- or 3-pole breaker connected to the high leg.
 