So, I'm working on a utility interactive solar home.
In the event that the utility goes down, there will be a battery bank so that the inverter can continue to provide power to panels located downstream from it. I am in the process of determining how much / which loads the inverter can supply in that circumstance, and wouldn't mind a second set of eyes.
There will be two 240V 4500W inverters, for a total of 9000W.
There will be two panels on the load side of those inverters.
It seems to me that there is scant little that this setup will power. Am I missing something obvious?
All values with zeroes are items the HO would like to have, but I don't think he can have.
More issues are, the recessed cans are typical resi 75W incandescent cans with little 13W lamps in them, but I have made the homeowner aware that I have to handle them as though they contained 75W lamps. It's going to be a topic of contention when I tell him that although supplying every can in his house is going to be around 7A, I have to pretend as though there are 43A in cans.
In the event that the utility goes down, there will be a battery bank so that the inverter can continue to provide power to panels located downstream from it. I am in the process of determining how much / which loads the inverter can supply in that circumstance, and wouldn't mind a second set of eyes.
There will be two 240V 4500W inverters, for a total of 9000W.
There will be two panels on the load side of those inverters.
It seems to me that there is scant little that this setup will power. Am I missing something obvious?
All values with zeroes are items the HO would like to have, but I don't think he can have.
More issues are, the recessed cans are typical resi 75W incandescent cans with little 13W lamps in them, but I have made the homeowner aware that I have to handle them as though they contained 75W lamps. It's going to be a topic of contention when I tell him that although supplying every can in his house is going to be around 7A, I have to pretend as though there are 43A in cans.