is it legel to put a 480 3 phase rec. above water?

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

There is no NEC prohibition for installing a 3 phase 480 volt receptacle above a source of water.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
the devil may be in the details.............................
note that if that "water" is in a swimming pool :)there are restrictions as shown in 680.8.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Is the "water" an ocean, lake, or river (i.e., is this a marina)? If so, 555 might have something to say about the situation.
 

truman

Member
the water is not a swimming pool

the water is not a swimming pool

the water is an open tank. I work at paper mill and the saftey committee wants to have these put in for sump pumps instead of running cords cross floors. (the sump pumps are not permanet)
 