chad lawson
Member
I am a cnc machine tool electronic technician with a strong industrial electric back ground. The company i work for is currenty expanding and would like to better understand the conductor size need for our new service and if our old service is adequate to continue running the old building. I have a 2500 amp 480/277 main breaker rated for continous duty, our new electrical service contractor has told us our current service which consists of 6 sets of 500kcmil conductors is not rated for continous duty rather about 1800 amps. i need to no if this is correct or not he mentioned our previous contractor used the 90c chart rather than the 60c. I will also be installing a seperate 2000amp 480/277 service for the new construction and would appreciate some help sizing this service. The problem i have is management wants to believe our new contractor but would like to be reasurred that our last contractor sized things wrong before we go through the expense of changing the conduits and conductors on our exsisting service.