I keep getting told that backfeeding the main panel is limited to 20% of the panel rating, for example, a 200 amp service can have a maximum 40 amp backfeed breaker. None of them can give the the code that they are referencing, and I can't find it.
 

iwire

Moderator
Staff member
Location
Massachusetts
I keep getting told that backfeeding the main panel is limited to 20% of the panel rating, for example, a 200 amp service can have a maximum 40 amp backfeed breaker. None of them can give the the code that they are referencing, and I can't find it.


That is true if your backfeeding a panel that already has full size utility feeder and your adding a solar array. This can be found in 690.
 