I have a 3-phase circuit of 500 kcmil, 5kV cable, 5960 ft in length.
Sixty (60) ft of which is located inside an Electrical Room at a temperature of 20 deg C. and the rest of the cable (5900 ft) is outside at a temperature of 15 deg C.
Because of the different ambient temperatures, the ampacities are different. I don't understand the Exception in Section 310.60 (B)(1). Do I rate the whole circuit (cable) at 20 deg C or 15 deg C?
The ampacity I will use will be calculated using Section (C)(4) Ambients Not in Tables.
Sixty (60) ft of which is located inside an Electrical Room at a temperature of 20 deg C. and the rest of the cable (5900 ft) is outside at a temperature of 15 deg C.
Because of the different ambient temperatures, the ampacities are different. I don't understand the Exception in Section 310.60 (B)(1). Do I rate the whole circuit (cable) at 20 deg C or 15 deg C?
The ampacity I will use will be calculated using Section (C)(4) Ambients Not in Tables.