I currently have fourteen (14) enclosures with Z purge systems on them and 9 are in CL1 DIV2 areas with a N2 purge on them, while the remaining are not purged at all. This CL1 DIV2 area is a warehouse type of building with four (4) large overhead doors, two (2) on opposing ends, and large ventilation fans on one end. That being said my feelings are that any fumes are minimized but the area is still classified as such.
My problem is that the non-purged enclosures are experiencing moisture build up and I want to use instrument air on them. While we are using N2 on the others, N2 is very expensive and I was wondering if I could switch these over to instrument air as well without violating any codes?
I have looked at NEC 500.2 Definition of "Purged & Pressurized" which only states that protective gas be used. Also NEC 505.8(B) "Purged & Pressurized", which of course does not state what is approved and ANSI/FPS 496.2003 does not state what is approved either.
I have seen from the purge panel manufacturer that instrument air is the most widely used, because N2 is so expensive.
Does anyone know if this has been done or is suitable?