I know, that is for commercial installations. According to code handbooks for 2008, 2005, and 2002 the wording is almost the same:
"Although the Code gives the previously described data on maximum permitted number of receptacle outlets in commercial, residential, institutional and other nonresidential installations, there are no such limitations on the number of receptacle outlets on residential branch circuits. There are reasons for this approach.
In 210.52, the Code specifies where and when receptacle outlets are required on branch circuits. Note that there are no specific requirements for receptacle outlets in commercial, industrial, and institutional installations other than for store show windows in 210.62 and roof A/C equipment in 210.63. There is the general rule that receptacles do have to be installed where flexible cords are used. In nonresidential buildings, if flexible cords are not used, there is no requirement for receptacle outlets. They have to be installed only where they are needed and the number of spacing of receptacles are completely up to the designer. But because the Code takes the position that receptacles in nonresidential buildings have to be installed where needed for connection of specific flexible cords, it demands that where such receptacles are installed each must be taken as a load of 180VA.
A different approach is used for receptacles in dwelling type occupancies. The Code simply assumes that cord connected appliances will always be used in all residential buildings and requires general purpose receptacle outlets of the number and spacing indicated in 210.52 and 210.60. These rules cover one family houses, apartments in multifamily houses, guest rooms in hotels and motels, living quarters in dormitories, and so forth. But because so many receptacle outlets are required in such occupancies and because use of plug connected loads is intermittent and has great diversity of load values and operating cycles, the Code notes at the bottom of Table 220.3(A) that the loads connected to such receptacles are adequately served by the branch circuit capacity required by 210.11, and no additional load calculations are required for such outlets."
So, by that...there is no limit to the number of outlets on a circuit in a dwelling unit...correct?