You can use the 6" depth per table 300.5 note 4 if using rigid pipe. GFI protection is still required.
Note 4. Where one of the wiring method types listed in Columns 1?3 is used for one of the circuit types in Columns 4 and 5, the shallowest depth of burial shall be permitted.
Rick