I have a customer who wants to buy a Unit Heater and the nameplate reads 208V 1 phase. How would this heater work / function at 240V 1 phase?

I have suggested he purchase a heater rated 240 / 208.

Thanks in advance.
 
A heater designed for use with 208 may over heat when connected to a 240 volt supply. The heat output will be 1.33% of nameplate.

The output percentage should be 133% not 1.33% as shown above.
 
Last edited:
091028-2226 eST

don's decimal point needs to move 2 places to the right.

That much over voltage might damage the heater. Very dependent on the design criteria for the heater.

.
 
I've had an old single phase 208 volt heater in my garage for years operating at or above 240 volts. Although I only use it occasionally it's still going.
 
I have an extension cord supplying my garage and it's worked fine for about 8 years.:grin:

That does not mean I would do that for a customer.
 
I have an extension cord supplying my garage and it's worked fine for about 8 years.:grin:

That does not mean I would do that for a customer.

ans your panel cover has proably been off as long :) (mine has)
 