I have a customer who wants to buy a Unit Heater and the nameplate reads 208V 1 phase. How would this heater work / function at 240V 1 phase?

I have suggested he purchase a heater rated 240 / 208.

Thanks in advance.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A heater designed for use with 208 may over heat when connected to a 240 volt supply. The heat output will be 1.33% of nameplate.

The output percentage should be 133% not 1.33% as shown above.
 
Last edited:

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
091028-2226 eST

don's decimal point needs to move 2 places to the right.

That much over voltage might damage the heater. Very dependent on the design criteria for the heater.

.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I've had an old single phase 208 volt heater in my garage for years operating at or above 240 volts. Although I only use it occasionally it's still going.
 

iwire

Moderator
Staff member
Location
Massachusetts
I have an extension cord supplying my garage and it's worked fine for about 8 years.:grin:

That does not mean I would do that for a customer.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I have an extension cord supplying my garage and it's worked fine for about 8 years.:grin:

That does not mean I would do that for a customer.

ans your panel cover has proably been off as long :) (mine has)
 