- Location
- Windsor, CO NEC: 2017
- Occupation
- Hospital Master Electrician
This is the commentary found in the 2008 hand book for 680.43(D)
Bonding and grounding requirements are similar to those in Parts I and II of Article 680 EXCEPT that metal to metal mounting on a common frame or base is an acceptable bonding method.
If 680.43 were a recreation of 680.26, then you could say that the two were similar. That does not mean that 680.26 supercedes the content of 680.43 due to brevity on .43's part.
The modification is not as significant as the duplicates: Look at (D)(2).That is the only modification described to Parts I and II of Article 680.
680.43(D)(2) would be a waste of ink, if 680.43 was not a surrogate for 680.26.
680.26 does not apply.
It's an interpretation call, I suppose, but I would hope that the panel comment above would modify the execution of your inspections on the matter.