We are in the process of up grading our elevator controls here at a small rural healthcare facility.
We are installing a new pump and controls for the elevator.
The hydraulic submersible pump for the elevator is a 20 hp, 3 ph, 208 volts.
The calculations for sizing the breaker for this come to around 147 amps, which rounded up to the next size is 150 amps.
The control panel states 80 amp service. So what is the proper sizing for this?
The elevator tech states that the 150 amp is too big, he suggested 125 amps.
Also, the breaker for the equipment is within 50' of the controls, so do we need a separate disconnect by the elevator equipment?