I see it the other way around.wire size has to be based on over-current protection device. . . .
I that case, the wire selected must be large enough that the 100a breaker provides adequate protection of it.. . . the Panle is already there and is equipped with a 100A breaker in it and their load is only about 30A. I have to use this panel.
I that case, the wire selected must be large enough that the 100a breaker provides adequate protection of it.
But do you have to keep the 100 amp breaker? Can you replace the panel's main breaker with a lower rated breaker? If so, I would go with a 50 amp breaker, or at highest a 60. That is based on 125% of the tranformer's secondary rating of 41.7 amps, and taking the next lower or next higher standard breaker. Then I would select a conductor rated for that ampacity (i.e., #8 if the breaker is 50 amps, #6 if it is 60 amps).The Panel is already there and is equipped with a 100A breaker in it and their load is only about 30A. I have to use this panel.