200 amp service...do you have to ground water and gas lines??? or just one and do you have to ground gas at point of entry of house...or anywhere in line??
			so bascially you only have to run a #4 copper to the water...then jumper to the gas
), then the bonding jumper to the gas line from the water line per 250.104(B) would be sized to a minimum of copper #6 or Al #4 by Table 250.122 for a 200A breaker. A supplemental Grounding Electrode (a ground rod for example) to the metal underground water pipe would still be required per 250.53(D)(2) with a grounding electrode conductor sized by Table 250.66 (copper #4 in this instance).
The NEC does not require a bonding jumper to gas piping.
You do not need to run anything larger than #6cu to a ground rod.
250.104(B) states that gas piping shall be bonded not that it should be bonded. Wouldn't that mean it is a requirement by the NEC?
I jump an appropriate sized wire from the gas line to the closest copper cold water line to the gas line.
1. 250.104(B) says 'gas piping that is likely to become energized shall be bonded...
2. ...to the service equipment enclosure, the grounded conductor at the service, the GEC where of sufficient size, or the one or more grounding electrodes used.'
Even if you have a 'likely to become energized' scenario, going to the closest copper cold water line would probably not meet the requirements of 250.104(B) [you would have to make this water pipe connection within 5 ft. of the water line entering the structure].
Moving on...the 2nd to last sentence in 250.104(B) permits the EGC for the circuit that is 'likely to energize' the piping to serve as the bonding means.
What exactly is happening at this structure that establishes a 'likely to become energized' situation? If an inspector is going to require bonding of the gas piping, then he should identify what hazard exists that makes this bonding necessary. Once he has so identified the hazard, then the EGC for the circuit should satisfy the requirements. Only if no EGC exists for the circuit creating the 'likelihood' is a separate bonding conductor necessary.
I'm willing to concede that the statement "likely to be energized" in 250.104(B) is very ambiguos, but as pointed out in "Soares Book on Grounding and Bonding" "Because metal piping systems are conductive, bonding all of them will provide additional safety."
Since the wording likely to energize is so ambiguous it can mean the gas fired dryer, gas water heater, gas range/oven, or the service entrance cable. I'd have to respectfully argue how can it be said that the gas pipe isn't likely to be energized? Sure we all do everything possible to prevent accidents from happening but that doesn't mean they don't and isn't that what the code is trying to prevent. Accidents turning into deaths.
A little off the subject just wondering if anybody else has ran across this, we have investigated a couple fires that were caused by the flexable gas pipes.
Lightning creates tiny holes in the flex and after that one good hit and is all it takes. Also The flex that started the fires were made by different manufactures