What kind of corrective action should be taken or at least moniotored in a building with a vast amount of 3 phasse VFD's. Thanks
Jim is right, of course. Harmonics will have an adverse affect on the supply voltage. But just how much depends on the specific circumstances.
And you need to know how much before you can determine what, if any, corrective action is required.
What can be done if it is deemed to be a problem?
Passive harmonic filters.
Active harmonic filters.
Replacing some of the VSDs with active front end units.
Polygonal transformers giving a 30deg shift for some of the VSDs.
All would require some system analysis to work out the best option(s).
I guess the best option is to ensure it isn't a problem in the first place. The design work can, or should be, done at the outset. We design and install VSD systems and often we have to agree contractual commitments to maximum distortion limits that will be achieved post install. This is prior to award of contract so you depend on getting it right by design. Or pay for the consequences if you don't.
That's fine if it is a new installation. But you don't often start with a clean sheet of paper. You have to make the best of what you've got.