I need to supply temporary 480V power to a load which is rated at 120A. The load will be connected to a disconnect.
All I have avaliable at the moment is an 125A breaker in MCC to protect cable, and an 100A disconnect. #2 AWG cable is going to be used, and most of run is in free air. Even if part of the run is in an MCC and room can we use the free air rating for this cable?
Even if temporary would you use 100A disconnect for a known load of 120A thinking that it may not draw that much?
Is 125A breaker large enough for this load? This load is continuous, so shouldnt we size breker and cable for 125% of load rating? Even if temporary?