Liquid flexible metal conduit with listed fittings shall be permitted in:
A)class 1 division 1 locations where necessary to employ flexible connections.
B)class 1 division 1 locations where the overcurrent protection in the circuit is limited to 10 A.
C)class 1 division 2 locations in lengths over 6 ft. without an equipment bonding jumper.
D) class 1 division 2 locations in lengths less than 6 ft. with an equipment bonding jumper.
I chose D) But it wasn't exact in wording so I'm not shure
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree with the answer D.

501.10(B)(2)(3) permits LFMC to be used with listed fittings.

Also 501.30(B) does not permit LFMC to be used as the sole EGC for class 1 div 2 locations.