Use table 250.66. The bonding jumper is based on the size of the service entrance conductors.
i am installing a 1200 amp three phase service how do i calculate the size of the service equipment bonding jumper, thank you all johneymac.:-?
This is actually a similar question. How/what do i size gec for the x0 to the ground rod? Xfrm is 277/480 primary:120/208 400amp secondary.
It doesn't have to be any larger than 6 cu or 4alum as long as its the only connection to a grounding electrode. If it is also hitting a ground ring,