1. You do have the (correct) circuit's white on the breaker's white terminal, and the pigtail on the panel neutral bus, right? And no shared-neutral use?I am doing a temporary lighting the engineer wants the incandescent lights on a gfi ckt breaker. When you go to turn on the ckt breaker it trips instantly.
That suggests a wiring mistake. Check my #1 above.regular ckt breakers work fine no shorts three ckt breakers doing the same thing
Well gee Wally, what about the total numbers of lamps on the String?
W=AV
I am doing a temporary lighting the engineer wants the incandescent lights on a gfi ckt breaker. When you go to turn on the ckt breaker it trips instantly. Any comments would help please
thank you
W=AV
Since it trips instantly,,,I'd be willing to bet it's not wired correctly. If it were overload, it would at least take several seconds.
Well ok, I thought about it, I reckon... I know... add that one extra lamp.
Dual duty GFCI - unintentional RECPT with light loads.
Some much can be left out sometimes in an OP (no offense).
Type of lamps, length of string, MWBC... Etc...
I'm going to go with a open short on the string, Rubbed open, or burnt open, which was already said.
Hey Be Safe out There!!! Happy Monday!
Aside from the obvious reasons given (short circuit, mis-wire, etc) are you using std. "A" bulbs or CFL's ? If they're CFL's that could be part or the total cause of your problem. In any case, I would start troubleshooting by unplugging the bulbs, turning on the GFCI breaker and see if the circuit holds. If it does, then start plugging in one bulb at a time and see what happens.