grounding

Status
Not open for further replies.

thorn949

Member
Location
california
we have a sig pac machine at work and the foil (the film) has static on it. my supervisors want me to install a ground rod? i siad no since supplemental grounds are useless and the earth is not an effective fault current path. the machine is already grounded and the roll of film should be discharged at the factory or something should be placed to discharge the static.so i guess i will try it to see what happens since the boss is always right ? any suggestions?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
They are now called Auxiliary electrodes. If they're paying I would install it anyway even if it does nothing. A EGC is still required to be run with the branch circuit conductors. Here is an older graphic:

1113918751_2.jpg
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
What, eactly, would they have you connect the wire for this extra rod to, and why wouldn't bonding that same surface/item it to the supply EGC suffice?
 

eric9822

Senior Member
Location
Camarillo, CA
Occupation
Electrical and Instrumentation Tech
Is this a packaging machine? If so winding or unwinding films frequently have issues with static electricity that needs to be dealt with. Do a search for "converting static control" and you will find a lot of vendors that deal with this problem.
 