Molded Case Circuit Breaker Nameplate Rating

Status
Not open for further replies.
I believe that means 126 amps and above requires 90C conductors
I agree.

But, the sizing of those conductors is still performed as if they were 75?C. There are no UL Listed device terminations for the 90?C column ampacities.
 