When you size transformer primary overcurrent protection up to 250% of primary current along with secondary protection at 125% of secondary current as per NEC table 450.3(B), are you required to size your primary conductors to the 250% rated breaker/fuse or can they be sized at 125% of primary current? I've always sized the primary conductors to the 250% rated OC device since I haven't found anything in the NEC that specifically says otherwise. However, in speaking with others on this subject I've found differing interpretations. Any clarification you could give me would be helpful.