I recently failed an inspection for the following.
Switch gear is Square D I-line, I installed a 200amp 208v breaker to feed a sub panel two suites over using a Cutler Hammer 200 amp 208v panel board with main lugs.
Inspector failed the install and cited the ISC ratings between Square D and cutler hammer wasn't the same and that I needed to install a sub panel with a main breaker to correct the violation. He didn't cite any specific code but I'm guessing he is referring to a UL listing.
Is he correct in calling the violation?
Switch gear is Square D I-line, I installed a 200amp 208v breaker to feed a sub panel two suites over using a Cutler Hammer 200 amp 208v panel board with main lugs.
Inspector failed the install and cited the ISC ratings between Square D and cutler hammer wasn't the same and that I needed to install a sub panel with a main breaker to correct the violation. He didn't cite any specific code but I'm guessing he is referring to a UL listing.
Is he correct in calling the violation?