To start with here is the set-up:
Privatly owned, two 13.2KV Delta to 480/277Y, 3000KVA Transtormers on two primary feeds(A/B) (Industrial Plant)
Main-Tie-Main Double Ended Switchboard
Swtbrd feeds three 1000Amp VFD controlled Chillers (one spare circuit)
Swtbrd set up: 4000A MB, 2x1200A BKR/4000A Tie BKR/2x1200A BKR/4000A MB
No nuetral loads served.
Customer wishes to close tie before opening main so as not to interrupt the service.
My questions are as follows:
Should this be teated as multiple seperately derived systems?
Since ther are no Nuetral loads must a Nuetral be created and be brought to the Distribution Board RE 250.20(B) & 250.24(C)?
How is the above question answered if XO is bonded at the transformer solidly or through a resistor?
Are we required to have GFI protection? Of Course IF there is no Nuetral in the board we can't install them.
Our engineer is checking some of this but I was wondering if anyone has got any feedback on the best/correct way to connect this sytem and provicde the customer with a safe/reliable system? (detect ground-faults without GFI Breakers and be code compliant).
What my gut is telling is this.
Since this system is seperately derived - grounding should be under 250.30. We can bond the thransformers XO at the double ended switchboard and assuming 11 sets of 500MCM would be per 250.102C or #2CU (we are exploring feeder duct). At the switchboard ground bus install the GEC to the existing Grounding Electrode System (it is quite extensive). Do not install GFI Breakers per 240.13(2)/230.95 Exception.
The 3000KVA transformers will match (Brand new from the same Manf.) so as long as we match rotation there should be no problem closing the tie breker before opening a feeder breaker. They do this thoughout the plant already (50 buidlings).
Of suorse this entire setup may push me into switchgear in lieu of a switchboard.
Please note that this installation is acuring at a "Supervised Industrial Installation" as defined in 240.2 and many of thier existing systems are ungrounded with ground fault monitoring only.
Thanks for any help,
GFH
Privatly owned, two 13.2KV Delta to 480/277Y, 3000KVA Transtormers on two primary feeds(A/B) (Industrial Plant)
Main-Tie-Main Double Ended Switchboard
Swtbrd feeds three 1000Amp VFD controlled Chillers (one spare circuit)
Swtbrd set up: 4000A MB, 2x1200A BKR/4000A Tie BKR/2x1200A BKR/4000A MB
No nuetral loads served.
Customer wishes to close tie before opening main so as not to interrupt the service.
My questions are as follows:
Should this be teated as multiple seperately derived systems?
Since ther are no Nuetral loads must a Nuetral be created and be brought to the Distribution Board RE 250.20(B) & 250.24(C)?
How is the above question answered if XO is bonded at the transformer solidly or through a resistor?
Are we required to have GFI protection? Of Course IF there is no Nuetral in the board we can't install them.
Our engineer is checking some of this but I was wondering if anyone has got any feedback on the best/correct way to connect this sytem and provicde the customer with a safe/reliable system? (detect ground-faults without GFI Breakers and be code compliant).
What my gut is telling is this.
Since this system is seperately derived - grounding should be under 250.30. We can bond the thransformers XO at the double ended switchboard and assuming 11 sets of 500MCM would be per 250.102C or #2CU (we are exploring feeder duct). At the switchboard ground bus install the GEC to the existing Grounding Electrode System (it is quite extensive). Do not install GFI Breakers per 240.13(2)/230.95 Exception.
The 3000KVA transformers will match (Brand new from the same Manf.) so as long as we match rotation there should be no problem closing the tie breker before opening a feeder breaker. They do this thoughout the plant already (50 buidlings).
Of suorse this entire setup may push me into switchgear in lieu of a switchboard.
Please note that this installation is acuring at a "Supervised Industrial Installation" as defined in 240.2 and many of thier existing systems are ungrounded with ground fault monitoring only.
Thanks for any help,
GFH