gfci with non gfi

Status
Not open for further replies.

mh183

Member
i always though it was an issue and remember seeing some in the nec maybe not exactly forbidden but not a good practice
 

TOOL_5150

Senior Member
Location
bay area, ca
i always though it was an issue and remember seeing some in the nec maybe not exactly forbidden but not a good practice

Its completly acceptable. Just as long as the line and load neutral are seperate - otherwise the GFCI will not work correctly.

The only wires to be kept apart are service conductors and feeders / branch circuits. [for residential]

~Matt
 

480sparky

Senior Member
Location
Iowegia
The only instance I can think this may be an issue is if the line side is the service entrance conductors, and the load side is GFI protected.

I don't think there's too many instances of this happening.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
680.23(F) has such restrictions on circuits for pool lighting.
 