Baseboard 240Vac heaters consume approximately 250w per lineal ft. The State Climate Zone rating for the location of your project is the first qualifying data required for local energy code baseline using resistant heating. For a quick answer using a prescriptive method, the following example will give an idea...
Climate Zone 1 (sea level) WA State......By Design= 8 BTU/sf....By Prescript=20 BTU/sf
Climate Zone 2 (High Elevation) 500'+.....By Design=12 BTU/sf....Prescription= 25 BTU/sf
Example 18' x 10' Room= 180 sf..........(1 w= 3.412 BTU)
Location at Climate Zone 1 by Prescription= 20 BTU x 180 sf / 3.412 = 1055w (4' heater)
A basic design would be to install a 20% higher output heater with wall thermostat. The larger heater warms the room quicker to the stat setting shutoff level. For a more energy saving choice, IR radiant heater would heat quicker and save up to 15% energy. rbj