100 KVA UPS Power Factor
Snowjob
Why do 100KVA UPS spec sheets quote input power factor as .98 and output power factor as .8?
Is there something I am missing here?
I think I answered my own question
The UPS is almost a pure resistive load from the input power perspective and can accomodate normal real world power factor (.8) at the output.
A VFD does the same thing. The switching power supply charges the UPS DC bus in unity with voltage(although it isn't a pretty sine wave) so you have close to unity power factor. The output power factor of the UPS depends on what is plugged into it. It can accommodate a load with .8 power factor at it's full nameplate power rating. If the supplied load has a lower power factor then .8 the UPS can't be fully loaded. Generators are this way. They rate generators in KW(real) at a given PF.
UPS calculation
UPS calculation
I am modelling the UPS for EDSA. Is this calculation below correct?
100KVA UPS spec sheets quote input power factor as .98 and output power factor as .8.
A 100kVA UPS rating implies the output power is 100KVA at 80 KW and 60 KVAR (.8 PF).
However how do you calculate the input draw? Assuming AC-AC efficiency of say 90% and PF of 99% (approximate as 1.00)
a) The 100KVA becomes 100 KW at the input because of the almost unity PF draw.
b) 100 KW/ .90 = 111 KW draw at the input 0 KVAR
am I right?
I would be more inclined to think that the ups could supply 80% of the input, than I would be inclined to think that you could supply it with 111% of what it is rated at.
If you put a scopemeter on the ups input and monitored the current I would bet money you wouldn't think it looks like a resistive load. It would look look pretty nasty, which is why harmonics can come into play.
Why would you assume KVA = KW ?
am I right?
I'm not sure where you come up with a & b, but assuming you have 100KVA, 80KW and 60KVAR, your power is 80KW. If you assume your .9 efficiency then your 80KW / .9 = 88KW reflected on the line side.
I took the 100 KVA figure on the output where PF is .8.
I tried to back calculate what this would require on the Input
On the input PF approx = .99 or 1.00 so I translated (perhaps mistakenly) the 100 KVA into a 100 KW draw at the input. Am I wrong for doing this?
They are two different things.
An output power factor of 0.8 limits output power to 80 kW.
The input pf depends on the input circuit topology. A 0.98 pf infers an active front end - the bit that converts ac to dc. Unless the manufacturer is being a bit loose on defining pf as just displacement rather than total.