1600 amp wire size calc
my question is about sizing conductors for a 1600 amp single phase service.
would 4 - # 500 MCM copper THWN-2 RATED FOR 90 C per phase be adequate
the run is less than 6 feet from ct cabinet to service disconnect
the allowable ampacities chart says 500 mMCM is good for 430 amps x 4 = 1720
Thanks for any comments
Sorry, but no. You can't use the 90C column for ampacity, unless all the components in the circuit are rated for 90C. The one that generally gets you is the terminations. They are seldom rated higher than 75C. So you can only use the 75C ampacity. Reference 110.14(C).
Thus, four 500's are only good for 4 x 380, or 1520 amps.
agree, but, to cover all possibilities: when you say "service disconnect" are you referring to one means (1600 amp breaker or bolt-lok switch, etc.) ?
charlieB
good answer.
We are looking into the lug rating (probably 75-c )
will have to increase conductor size, thankfully it is a very short run
Why dont manufactures just use 90-c rated lugs ?
Thanks again for an A++++ answer
The lug itself may actually be rated 90 C, but the equipment (breakers, fused disconnects, etc) it is connected to will not be.
Why don't manufactures just use 90-c rated lugs ?
It would be difficult to make a breaker that could handle a 90 C conductor and still not trip early due to heat.
That said, I agree with the others, you will need 600 copper or a reduction of the over current protection.
Probably why this is so uncommon is the fact a 1000 amp 3 phase service would give you about the same amount of KVA, and wire size would be much reduced., I have seen a few but only in a rural area where 3 phase wasn't available.