LUIS FERNANDEZ
Is there any code requirement either ADA or NFPA 101 for having emergency lighting in single person toilets.
In the event of power supply failure, an emergency electrical system shall automatically illuminate the following areas:
1. Aisles and unenclosed egress stairways in rooms and spaces that require two or more means of egress.
2. Corridors, exit enclosures and exit passageways in buildings required to have two or more exits.
3. Exterior egress components at other than the level of exit discharge until exit discharge is accomplished for buildings required to have two or more exits.
4. Interior exit discharge elements, as permitted in Section 1024.1 in buildings required to have two or more exits.
5. Exterior landings, as required by Section 1008.1.5, for exit discharge doorways in buildings required to have two or more exits.
When you have to go, you want the head close by, not remote.I'd offer the upgrade of at least a remote head.
Verrrrrrrrrrrrry funny. :grin:When you have to go, you want the head close by, not remote.