Power for store sign...in the parking lot???

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
need a little more :)
are you talking about open wiring ? we definitely need some detail for an opinion...
 

sparks2000

Senior Member
Location
Chicago,IL
I was walking home when I saw a WP box with, looked like #12 THHN coming out of the top of box and then ran overhead to a sign that was not attached to the building... does the NEC let you do this?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
no THHN :grin:, but THWN :)
If properly terminated (as in supported), spaced, etc. it is Code permissible.
Take a look at sections such as 225.11, 225.12, 225.14
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
not much different from a POCO open span of wire feeding a service........
 