electgut21:
You need to look closely at the plug and socket failures and try to determined where the greatest heat was generated.
If the failure was at the contact interface between the plug and socket, then do some contact voltage drop measurements under operating load conditions. It is possible you have some defective components, or excessive current for the plug and socket.
Voltage drop measurement must be made directly from the base elements of the plug and socket, not from the wires. This eliminates the voltage drop of the wire to plug component interface.
When I ran the tests of my earlier post I used a standard 120 V plug and socket because I had those at home. I will look at the shop to see if I have a large twist lock pair to test.
.