Now what about service calc's and the range
Now what about service calc's and the range
Now that we have digressed a bit!
I would like to know various opinions as to how to add the calc for the range in the main service of a single family dwelling.
Lets take a 12.9 KV Range nameplate.
1) do we apply table 220.55 and it states 8KW and add 5% because it is over 12KV. ( I rounded to the higher)
2) or do we take the nameplate at 12.9KV as per 220.82 (B) (4) 2005 NEC
Now what about service calc's and the range
Now that we have digressed a bit!
I would like to know various opinions as to how to add the calc for the range in the main service of a single family dwelling.
Lets take a 12.9 KV Range nameplate.
1) do we apply table 220.55 and it states 8KW and add 5% because it is over 12KV. ( I rounded to the higher)
2) or do we take the nameplate at 12.9KV as per 220.82 (B) (4) 2005 NEC