joshgarcia
Member
In the power plant I work at we have a North and a South battery vault which feed a subpanel that provides the control power to our 12kv switchgear. There is a transfer switch to switch from N. to S. vault power. To avoid tripping the plant offline when I switched from South to North I installed jumpers across the N. feed to the load terminals (after checking my difference in potential) inside the transfer switch to prevent an interruption in power to the subpanel being it is not a make before break switch. There were spare lugs at each termination point making it both safe and easy. Now my supervisor wishes to install a disconnect or circuit breaker in line with this "jumper" to avoid having to work the circuit live inside the transfer switch when doing our vault swaps. My question is: do we need to size our "jumper circuit" to the vault overcurrent protection sizing which is 200A? I would think so but hoping to be able to order smaller and cheaper! I have never seen the amp meters show more than 8 Amps being drawn from the subpanel, but I know the potential is there.