As a follow up question, what would you do in the case where you have a larger room, where it is actually labeled as three separate rooms (the "kitchen" portion only takes up half the space square footage-wise)? Would you still make all receptacles GFCI?
Not applicable. This is not residential. See post #6....most likely the dining room, so you can still have those receptacles on your SABC.
Not applicable. This is not residential. See post #6.
Does anybody agree with me that this interpretation of a break room being a kitchen is a little much, and goes way beyond the intent of the code? I don't have a problem with designing for GFCIs in a break room or lounge, it's not any extra effort on my part, but imo the code intent is most likely for actual kitchens, i.e. food prep areas with floor drains that are likely to be mopped nightly or sprayed down. What's the purpose of a GFCI nowhere near a sink in a staff lounge or break room? Just sayin.
Just thought I'd give my two cents, although so far seems like everyone disagrees with my viewpoint
EDIT: Btw I should clarify that of course we still need to provide GFCI for the microwave and toaster and what not over by the sink, I'm strictly speaking of requiring GFCIs for the general purpose receptacles in the room.
Not really. Many people spend just as much if not more time in the office as they do at home (subtract sleep time) I get to the office at 6:45 stay until 4:30, so around 10 hours. Go home take my son to baseball, go bowling, whatever, get home around 7 in bed by 11, only 4 hours.
You said GFI receptacle, I will assume GFCI, minor I know but major price difference between what a GFCI receptacle verses wha a GFI breaker would be.
Don't forget to have it tamper proof as well, also new in 08'.
I'm not quite following why that means that general purpose receptacles in a staff lounge/break room greater than 6 ft. from a sink should require GFCI protection.
EDIT: Ah I see, I think you were only addressing why it could be considered a kitchen, not so much the GFCI aspect. Sorry...long day.
Not all jurisdictions are enforcing the 08' TR receptacle requirement. Our State has the requirement, but if you do work in an area that does their own electrical inspections, then you will find that they have not accepted the 08' TR requirement.
My understanding is TR (Tamperproof) is also required for some commercial. Example of some: Childcare center, Children's hospital. Outside of that, they "may not" require them--depends on the jurisdiction. A city here has the exact rule I stated above. They do not require them in residential or commercial--unless the commercial building is as described in "Example."I thought TR was for Dwelling Units, 406.11.
My understanding is TR (Tamperproof) is also required for some commercial. Example of some: Childcare center, Children's hospital. Outside of that, they "may not" require them--depends on the jurisdiction. A city here has the exact rule I stated above. They do not require them in residential or commercial--unless the commercial building is as described in "Example."
is that an nec issue or building code?
NEC 517.18 (c)