value fo conductors
Derick
Point to point Method of short circuit calculation: how the value of conductors is calculated from?
Note p.8 says:1/z (per 1 foot) which is found based on R an X in IEEE 241-1990.
I don't get it.
Ex.500 mcm in steel conduit :
Table 9 NEC for 500 mcm
X=0.048 and R=0.029
So according to note p.8
1/(0.029+0.048)=0.077
What am I doing wrong here?
I don't get it.
X=0.048 and R=0.029
Well that number come up in the Grey book:
IEEE recommended practice for electric power systems in commercial buildings. (Color Book Series - Gray Book)
I don't have access but will study what they do allow :)
Could you put the second equation in or reference the complete one to us, Lay men and women
As the math sits you used both R and x for a Z... where's the 1000 ft pluging in.
I'm sure Im missing something as well here, Clue me in... other's can play along at there will. :)
Your right I just asked the teacher!
Sorry I missed table 9 reference, plug it in.
1/(0.029+0.048)= 12.98
Yes I made typo mistake in calc.
But what I am trying to find out is :
How to calculate "C" values for conductors by using NEC only.
Also IEEE 241-1990 table 2 shows 3 single conductors.On 3ph 4w
system neutral is CCC so there are 4 conductors in the raceway.
(unbalanced load)
Well if I used Table 9 to obtain conductor impedance the values are shown per 1000 LF,so to obtain per 1 LF it would be: Z= X+R/ 1000 per linear foot
Am i on the right track with finding Z?
Thanks
I don't get it.
X=0.048 and R=0.029
Z=sqrt(R^2+X^2)